Hello
I was wondering if it was "allowed" to change the thermal conduction of a material without changing other parameters. I found a wood material (Spruce, radial) in the Fraunhofer database but the thermal conduction is to low. Could i just copy this material and adjust the conductivity without changing diffusiion properties?
best regards
Editing existing materials
-
Christian Bludau
- WUFI SupportTeam IBP

- Posts: 1246
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: Editing existing materials
Generally spoken it is no problem to change the heat conduction of a material. But you have to make sure, that the other material parameters are still consistent. The higher conductivity can be due to a higher density which also can influence the diffusion properties.
Please also see the material softwood, maybe that fits better.
Christian
Please also see the material softwood, maybe that fits better.
Christian
-
fostertom
- WUFI User

- Posts: 44
- Joined: Thu Jun 20, 2013 5:16 am -1100
- Location: Dartmoor, Devon, UK
- Contact:
Re: Editing existing materials
An edit I would like to do: ordinary white EPS 0.04 vs graphited EPS 0.32. There seems none of the latter in the database but is now much used. It has same density and , I'd have thought, all other properties apart from addition of graphite powder. So would a simple change from 0.04 to 0.32 be reliable?
BTW, why is ordinary EPS so high (0.04). All UK data says 0.038, even after the more conservative test criteria imposed a few years ago. and graphited EPS is often 0.031. Is this PHPP-style pessimism applied to 'generic' products?
BTW, why is ordinary EPS so high (0.04). All UK data says 0.038, even after the more conservative test criteria imposed a few years ago. and graphited EPS is often 0.031. Is this PHPP-style pessimism applied to 'generic' products?
-
Christian Bludau
- WUFI SupportTeam IBP

- Posts: 1246
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: Editing existing materials
Hello Tom,
be careful by changing the thermal conductivity. If there is a table for the moisture depending conductivity (extended material functions) you have to change all values, not only the dry value in the basic values on the lift. I usually change the increase of conductivity for 0.032 proportional to the rise of the 0.04.
Christian
be careful by changing the thermal conductivity. If there is a table for the moisture depending conductivity (extended material functions) you have to change all values, not only the dry value in the basic values on the lift. I usually change the increase of conductivity for 0.032 proportional to the rise of the 0.04.
Christian
-
fostertom
- WUFI User

- Posts: 44
- Joined: Thu Jun 20, 2013 5:16 am -1100
- Location: Dartmoor, Devon, UK
- Contact:
Re: Editing existing materials
Yes I thought I'd do it proportionally.