Vented Cavities - Specifying Air Source

Post by NTP »

From the help file I see that when you vent a cavity the ACH specified assumes that the air in the space is vented with exteior air. Is it possible to specify that the air in the cavity is vented with air from the interior (i.e. air leakage). I am currently using WUFI 4.2, is this something that can be specified with a newer version?

Thanks,

N
Daniel
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 146
Joined: Tue Jul 19, 2005 2:50 am -1100
Location: Fraunhofer IBP, Holzkirchen
Contact:

Ventilation with interior air in version 5

Post by Daniel »

Yes - in version 5 we added the possibility to choose if the air from the indoor or outdoor climate should be used.

Daniel
Dr.-Ing. Daniel Zirkelbach, Deputy Head of Department Hygrothermics, IBP Holzkirchen