Re: Admissible water content in g/m² for wood-fibre insulation.
More information can be found here - but the topic is still ongoing:
https://wufi.de/de/wp-content/uploads/s ... Report.pdf
https://wufi.de/de/wp-content/uploads/s ... Report.pdf
- Fri Nov 21, 2025 5:04 am -1100
- Forum: WUFI Pro
- Topic: Admissible water content in g/m² for wood-fibre insulation.
- Replies: 2
- Views: 1417
Re: Admissible water content in g/m² for wood-fibre insulation.
Dear Alexandre,
This is not an easy question to answer. According to CSTB SimHuBat 7.6 (in France), 23% moisture content is permissible for non-load-bearing wood-based materials.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are ...
This is not an easy question to answer. According to CSTB SimHuBat 7.6 (in France), 23% moisture content is permissible for non-load-bearing wood-based materials.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are ...
- Fri Nov 21, 2025 5:00 am -1100
- Forum: WUFI Pro
- Topic: Grenzwertfeuchtigkeit Holzfasereinblasdämmung als Innendämmung
- Replies: 2
- Views: 982
Re: Grenzwertfeuchtigkeit Holzfasereinblasdämmung als Innendämmung
Hallo Herr Hartmann,
dieses Bewertungskriterium ist im Moment ein bisschen in der Schwebe. Nach WTA gilt die dortige Grenzkurve nur für Massivholz.
Neuere Forschungsergebnisse wie z.B. ThermNat zeigen allerdings, dass viele der dort untersuchten Holzfaserdämmstoffe genauso oder sogar beständiger ...
dieses Bewertungskriterium ist im Moment ein bisschen in der Schwebe. Nach WTA gilt die dortige Grenzkurve nur für Massivholz.
Neuere Forschungsergebnisse wie z.B. ThermNat zeigen allerdings, dass viele der dort untersuchten Holzfaserdämmstoffe genauso oder sogar beständiger ...
- Fri Nov 21, 2025 4:48 am -1100
- Forum: WUFI France
- Topic: Teneur d'eau admise en g/m2 dans une isolation en laine de bois
- Replies: 1
- Views: 627
Re: Teneur d'eau admise en g/m2 dans une isolation en laine de bois
Dear Alexandre,
this is not an easy question to answer. According to CSTB SimHuBat 7.6, 23% by mass is permissible for non-load-bearing wood-based materials in France.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are even more ...
this is not an easy question to answer. According to CSTB SimHuBat 7.6, 23% by mass is permissible for non-load-bearing wood-based materials in France.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are even more ...
- Thu Sep 25, 2025 4:29 am -1100
- Forum: WUFI France
- Topic: Résultats toiture végétalisée défavorables
- Replies: 1
- Views: 11495
Re: Résultats toiture végétalisée défavorables
Dear Mr. Axoé,
you're right, via the membranes no water can be transportet into the assembly. I guess, the rise of moisture is caused by convergence failures and numerical problems.
Please try in a first step to replace the soil by the substrate layers which are available in the data base ...
you're right, via the membranes no water can be transportet into the assembly. I guess, the rise of moisture is caused by convergence failures and numerical problems.
Please try in a first step to replace the soil by the substrate layers which are available in the data base ...
- Wed May 21, 2025 2:23 am -1100
- Forum: WUFI Pro
- Topic: WUFI Dachschalung - Auffeuchtung von außen im Winter bei manchen Klimadatensätzen
- Replies: 1
- Views: 12249
Re: WUFI Dachschalung - Auffeuchtung von außen im Winter bei manchen Klimadatensätzen
Hallo Herr Hauser,
diffusionsoffene (in Deutschland häufig nachweisfreie) Dachkonstruktionen weisen tatsächlich im Außenbereich häufig Feuchten auf, die zumindest die pauschalen Grenzwerte der DIN 68800 überschreiten (20 oder 18 M.-% Holzfeuchte). Die Simulationsergebnisse decken sich dabei mit ...
diffusionsoffene (in Deutschland häufig nachweisfreie) Dachkonstruktionen weisen tatsächlich im Außenbereich häufig Feuchten auf, die zumindest die pauschalen Grenzwerte der DIN 68800 überschreiten (20 oder 18 M.-% Holzfeuchte). Die Simulationsergebnisse decken sich dabei mit ...
- Wed Apr 16, 2025 3:22 am -1100
- Forum: Material
- Topic: Maximale Relative Feuchte Kalkputz/Kalkzementputz
- Replies: 1
- Views: 17062
Re: Maximale Relative Feuchte Kalkputz/Kalkzementputz
Hallo Sebastian,
also der einfache Grenzwert aus WTA 6-4 von 95 % kann auf jeden Fall auch für diese Materialien angesetzt werden. Ich vermute aber, dieser reicht nicht aus oder?
viele Grüße
Daniel
also der einfache Grenzwert aus WTA 6-4 von 95 % kann auf jeden Fall auch für diese Materialien angesetzt werden. Ich vermute aber, dieser reicht nicht aus oder?
viele Grüße
Daniel
- Mon Mar 03, 2025 8:54 pm -1100
- Forum: WUFI France
- Topic: Analyse du diagramme "Local Hygrothermal Load"
- Replies: 2
- Views: 95457
Re: Analyse du diagramme "Local Hygrothermal Load"
Dear Guillaume,
the mould growth criteria of 80 % RH and according to the LIM curves or also the VTT / Finmould model are ALL related to the interior surface - but not to the interior part of constructions and especially not for the exterior cold part of the insulation layer.
The WTA guideline 6 ...
the mould growth criteria of 80 % RH and according to the LIM curves or also the VTT / Finmould model are ALL related to the interior surface - but not to the interior part of constructions and especially not for the exterior cold part of the insulation layer.
The WTA guideline 6 ...
- Thu Feb 27, 2025 8:57 pm -1100
- Forum: WUFI 2D
- Topic: Luftwechselrate bei Dächern mit hinterlüftungsebene nach DIN 4108-3
- Replies: 1
- Views: 30722
Re: Luftwechselrate bei Dächern mit hinterlüftungsebene nach DIN 4108-3
Sehr geehrter Herr Bickenbach,
die diffusionsoffenen Dächer sind schon sehr lange als nachweisfreie Konstruktionen in der Norm und basieren auf empirischen Erfahrungen, nicht auf Simulationen.
Typische Luftwechselraten auf Basis der geforderten Querschnitte / Öffnungen sind kaum bekannt - ich ...
die diffusionsoffenen Dächer sind schon sehr lange als nachweisfreie Konstruktionen in der Norm und basieren auf empirischen Erfahrungen, nicht auf Simulationen.
Typische Luftwechselraten auf Basis der geforderten Querschnitte / Öffnungen sind kaum bekannt - ich ...
- Fri Jan 10, 2025 5:50 am -1100
- Forum: Material
- Topic: Free water saturation
- Replies: 1
- Views: 22777
Re: Free water saturation
Hi Valeria,
nice to hear from you ;-)
Free saturation means the amount of water whichs is absorbed by the material when you store it under water until mass consistancy (absolute amount - you substract only the dry density of the material). We measure the free saturation according to EN ISO 16535 ...
nice to hear from you ;-)
Free saturation means the amount of water whichs is absorbed by the material when you store it under water until mass consistancy (absolute amount - you substract only the dry density of the material). We measure the free saturation according to EN ISO 16535 ...
- Fri Jan 10, 2025 5:33 am -1100
- Forum: WUFI France
- Topic: Relachement d'humidité periodique dans salle humide
- Replies: 1
- Views: 24538
Re: Relachement d'humidité periodique dans salle humide
Dear Guillaume,
I understand your considerations concerning the moisture load. However, the EN 13788 only requires the "moisture load" this is added to the absolute moisture content of the exterior air and "converted" to the indoor air temperature. A constant indoor climate according to EN 13788 ...
I understand your considerations concerning the moisture load. However, the EN 13788 only requires the "moisture load" this is added to the absolute moisture content of the exterior air and "converted" to the indoor air temperature. A constant indoor climate according to EN 13788 ...
- Mon Sep 23, 2024 5:10 am -1100
- Forum: Material
- Topic: Wood rot threshold for chemically-treated wood
- Replies: 2
- Views: 25140
Re: Wood rot threshold for chemically-treated wood
Hi David,
I'm not aware of any limit values for treated would in standards. Normally the information is more like: if you exceed the normal limit value you need chemical protection.
However, 20 % is pretty conservative. The WTA guideline 6-8 allows clearly higher values depending on the ...
I'm not aware of any limit values for treated would in standards. Normally the information is more like: if you exceed the normal limit value you need chemical protection.
However, 20 % is pretty conservative. The WTA guideline 6-8 allows clearly higher values depending on the ...
- Thu May 16, 2024 8:46 am -1100
- Forum: WUFI Pro
- Topic: Wahl Außenklima
- Replies: 1
- Views: 26145
Re: Wahl Außenklima
Hallo Thomas,
tatsächlich würden wir - uns so würde ich es auch aus der Norm herauslesen - zunächst mal empfehlen, die Bemessung einfach mit dem für die jeweilige Region gültigen Referenzklima durchzuführen. Für normale Belastungen ist der jeweilige Standort ausreichend repräsentativ (früher haben ...
tatsächlich würden wir - uns so würde ich es auch aus der Norm herauslesen - zunächst mal empfehlen, die Bemessung einfach mit dem für die jeweilige Region gültigen Referenzklima durchzuführen. Für normale Belastungen ist der jeweilige Standort ausreichend repräsentativ (früher haben ...
- Mon Feb 26, 2024 9:45 pm -1100
- Forum: General
- Topic: Floor above car park
- Replies: 1
- Views: 24930
Re: Floor above car park
Dear Jacob,
do I understand right: exposed means: without roof? Exposed to rain and radiation?
However, the available mould growth models (Bio and VTT) are both only validated for interior surfaces and "contain" species, which only can survive inside (no frost, no UV radiation, no rain etc ...
do I understand right: exposed means: without roof? Exposed to rain and radiation?
However, the available mould growth models (Bio and VTT) are both only validated for interior surfaces and "contain" species, which only can survive inside (no frost, no UV radiation, no rain etc ...