Search found 150 matches
- Fri Jun 05, 2026 12:11 am -1100
- Forum: WUFI Pro
- Topic: Interior insulation in masonry wall
- Replies: 5
- Views: 242
Re: Interior insulation in masonry wall
Thanks for the reply. I really appreciate it.
when I want to calculate the final conditions (water content) of the original wall (just stone wall and render) which will be the initial conditions of the proposed wall (with interior insulation), do I also need to set an air leakage rate (q50) on ...
- Fri Jun 05, 2026 12:06 am -1100
- Forum: WUFI Pro
- Topic: Interior insulation in masonry wall
- Replies: 5
- Views: 242
Re: Interior insulation in masonry wall
Dear Alberto,
you can introduce a 1 % rain source and check what is happening. However, cracks at the window will lead to local moisture entry - and problems around the window, but not to moisture entry in the middle of the wall.
If there are cracks or the rain protection of the render is too ...
you can introduce a 1 % rain source and check what is happening. However, cracks at the window will lead to local moisture entry - and problems around the window, but not to moisture entry in the middle of the wall.
If there are cracks or the rain protection of the render is too ...
- Wed Jun 03, 2026 4:26 am -1100
- Forum: WUFI Pro
- Topic: Interior insulation in masonry wall
- Replies: 5
- Views: 242
Re: Interior insulation in masonry wall
Hi Alberto,
1- Should I add 1 % of driving rain? if yes, where should I place it? In the outermost 5mm of the render in contact with external ambient?
ANSWER: No - this is only used in case of EWIS / EIFS or facade claddings, where rain can run behind the most exterior layer, but not for rendered ...
1- Should I add 1 % of driving rain? if yes, where should I place it? In the outermost 5mm of the render in contact with external ambient?
ANSWER: No - this is only used in case of EWIS / EIFS or facade claddings, where rain can run behind the most exterior layer, but not for rendered ...
- Fri Mar 06, 2026 5:20 am -1100
- Forum: Climate
- Topic: Hinterlüftetes Steildach
- Replies: 1
- Views: 8939
Re: Hinterlüftetes Steildach
Hallo Herr Ansari,
ich vermute, dass die Schalung unter der V13 im Wesentlichen die Gleichgewichtsfeuchten zur Außenluft – einschließlich einer gewissen Unterkühlung der Eindeckung – bekommt. Sprich: Die Feuchtegehalte würden sich vermutlich sehr ähnlich einstellen, wenn Sie nur eine Schalung mit ...
ich vermute, dass die Schalung unter der V13 im Wesentlichen die Gleichgewichtsfeuchten zur Außenluft – einschließlich einer gewissen Unterkühlung der Eindeckung – bekommt. Sprich: Die Feuchtegehalte würden sich vermutlich sehr ähnlich einstellen, wenn Sie nur eine Schalung mit ...
- Fri Nov 21, 2025 5:19 am -1100
- Forum: WUFI Pro
- Topic: Grenzwertfeuchtigkeit Holzfasereinblasdämmung als Innendämmung
- Replies: 2
- Views: 10081
Re: Grenzwertfeuchtigkeit Holzfasereinblasdämmung als Innendämmung
Weitere Informationen gibt es im Projektbericht - aber das Thema wird aktuell auch noch weiter bearbeitet:
https://wufi.de/de/wp-content/uploads/s ... ericht.pdf
https://wufi.de/de/wp-content/uploads/s ... ericht.pdf
- Fri Nov 21, 2025 5:19 am -1100
- Forum: WUFI Pro
- Topic: Admissible water content in g/m² for wood-fibre insulation.
- Replies: 2
- Views: 11462
Re: Admissible water content in g/m² for wood-fibre insulation.
More information can be found here - but the topic is still ongoing:
https://wufi.de/de/wp-content/uploads/s ... Report.pdf
https://wufi.de/de/wp-content/uploads/s ... Report.pdf
- Fri Nov 21, 2025 5:04 am -1100
- Forum: WUFI Pro
- Topic: Admissible water content in g/m² for wood-fibre insulation.
- Replies: 2
- Views: 11462
Re: Admissible water content in g/m² for wood-fibre insulation.
Dear Alexandre,
This is not an easy question to answer. According to CSTB SimHuBat 7.6 (in France), 23% moisture content is permissible for non-load-bearing wood-based materials.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are ...
This is not an easy question to answer. According to CSTB SimHuBat 7.6 (in France), 23% moisture content is permissible for non-load-bearing wood-based materials.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are ...
- Fri Nov 21, 2025 5:00 am -1100
- Forum: WUFI Pro
- Topic: Grenzwertfeuchtigkeit Holzfasereinblasdämmung als Innendämmung
- Replies: 2
- Views: 10081
Re: Grenzwertfeuchtigkeit Holzfasereinblasdämmung als Innendämmung
Hallo Herr Hartmann,
dieses Bewertungskriterium ist im Moment ein bisschen in der Schwebe. Nach WTA gilt die dortige Grenzkurve nur für Massivholz.
Neuere Forschungsergebnisse wie z.B. ThermNat zeigen allerdings, dass viele der dort untersuchten Holzfaserdämmstoffe genauso oder sogar beständiger ...
dieses Bewertungskriterium ist im Moment ein bisschen in der Schwebe. Nach WTA gilt die dortige Grenzkurve nur für Massivholz.
Neuere Forschungsergebnisse wie z.B. ThermNat zeigen allerdings, dass viele der dort untersuchten Holzfaserdämmstoffe genauso oder sogar beständiger ...
- Fri Nov 21, 2025 4:48 am -1100
- Forum: WUFI France
- Topic: Teneur d'eau admise en g/m2 dans une isolation en laine de bois
- Replies: 1
- Views: 14377
Re: Teneur d'eau admise en g/m2 dans une isolation en laine de bois
Dear Alexandre,
this is not an easy question to answer. According to CSTB SimHuBat 7.6, 23% by mass is permissible for non-load-bearing wood-based materials in France.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are even more ...
this is not an easy question to answer. According to CSTB SimHuBat 7.6, 23% by mass is permissible for non-load-bearing wood-based materials in France.
Until now, the WTA curve has actually been intended for softwood. However, many wood fiber insulation materials are even more ...
- Thu Sep 25, 2025 4:29 am -1100
- Forum: WUFI France
- Topic: Résultats toiture végétalisée défavorables
- Replies: 1
- Views: 30376
Re: Résultats toiture végétalisée défavorables
Dear Mr. Axoé,
you're right, via the membranes no water can be transportet into the assembly. I guess, the rise of moisture is caused by convergence failures and numerical problems.
Please try in a first step to replace the soil by the substrate layers which are available in the data base ...
you're right, via the membranes no water can be transportet into the assembly. I guess, the rise of moisture is caused by convergence failures and numerical problems.
Please try in a first step to replace the soil by the substrate layers which are available in the data base ...
- Wed May 21, 2025 2:23 am -1100
- Forum: WUFI Pro
- Topic: WUFI Dachschalung - Auffeuchtung von außen im Winter bei manchen Klimadatensätzen
- Replies: 1
- Views: 24132
Re: WUFI Dachschalung - Auffeuchtung von außen im Winter bei manchen Klimadatensätzen
Hallo Herr Hauser,
diffusionsoffene (in Deutschland häufig nachweisfreie) Dachkonstruktionen weisen tatsächlich im Außenbereich häufig Feuchten auf, die zumindest die pauschalen Grenzwerte der DIN 68800 überschreiten (20 oder 18 M.-% Holzfeuchte). Die Simulationsergebnisse decken sich dabei mit ...
diffusionsoffene (in Deutschland häufig nachweisfreie) Dachkonstruktionen weisen tatsächlich im Außenbereich häufig Feuchten auf, die zumindest die pauschalen Grenzwerte der DIN 68800 überschreiten (20 oder 18 M.-% Holzfeuchte). Die Simulationsergebnisse decken sich dabei mit ...
- Wed Apr 16, 2025 3:22 am -1100
- Forum: Material
- Topic: Maximale Relative Feuchte Kalkputz/Kalkzementputz
- Replies: 1
- Views: 29123
Re: Maximale Relative Feuchte Kalkputz/Kalkzementputz
Hallo Sebastian,
also der einfache Grenzwert aus WTA 6-4 von 95 % kann auf jeden Fall auch für diese Materialien angesetzt werden. Ich vermute aber, dieser reicht nicht aus oder?
viele Grüße
Daniel
also der einfache Grenzwert aus WTA 6-4 von 95 % kann auf jeden Fall auch für diese Materialien angesetzt werden. Ich vermute aber, dieser reicht nicht aus oder?
viele Grüße
Daniel
- Mon Mar 03, 2025 8:54 pm -1100
- Forum: WUFI France
- Topic: Analyse du diagramme "Local Hygrothermal Load"
- Replies: 2
- Views: 108592
Re: Analyse du diagramme "Local Hygrothermal Load"
Dear Guillaume,
the mould growth criteria of 80 % RH and according to the LIM curves or also the VTT / Finmould model are ALL related to the interior surface - but not to the interior part of constructions and especially not for the exterior cold part of the insulation layer.
The WTA guideline 6 ...
the mould growth criteria of 80 % RH and according to the LIM curves or also the VTT / Finmould model are ALL related to the interior surface - but not to the interior part of constructions and especially not for the exterior cold part of the insulation layer.
The WTA guideline 6 ...
- Thu Feb 27, 2025 8:57 pm -1100
- Forum: WUFI 2D
- Topic: Luftwechselrate bei Dächern mit hinterlüftungsebene nach DIN 4108-3
- Replies: 1
- Views: 43101
Re: Luftwechselrate bei Dächern mit hinterlüftungsebene nach DIN 4108-3
Sehr geehrter Herr Bickenbach,
die diffusionsoffenen Dächer sind schon sehr lange als nachweisfreie Konstruktionen in der Norm und basieren auf empirischen Erfahrungen, nicht auf Simulationen.
Typische Luftwechselraten auf Basis der geforderten Querschnitte / Öffnungen sind kaum bekannt - ich ...
die diffusionsoffenen Dächer sind schon sehr lange als nachweisfreie Konstruktionen in der Norm und basieren auf empirischen Erfahrungen, nicht auf Simulationen.
Typische Luftwechselraten auf Basis der geforderten Querschnitte / Öffnungen sind kaum bekannt - ich ...
- Fri Jan 10, 2025 5:50 am -1100
- Forum: Material
- Topic: Free water saturation
- Replies: 1
- Views: 34802
Re: Free water saturation
Hi Valeria,
nice to hear from you ;-)
Free saturation means the amount of water whichs is absorbed by the material when you store it under water until mass consistancy (absolute amount - you substract only the dry density of the material). We measure the free saturation according to EN ISO 16535 ...
nice to hear from you ;-)
Free saturation means the amount of water whichs is absorbed by the material when you store it under water until mass consistancy (absolute amount - you substract only the dry density of the material). We measure the free saturation according to EN ISO 16535 ...