Studying indoor insulation
Posted: Mon May 30, 2011 8:26 pm -1100
Hello everyone,
I am a beginner with WUFI 3D and I am wondering a few questions concerning the analysis of the results.
The pursposes of my study are :
- First to compare to types of indoor insulation (rockwool + vapor barrier, 10 cm, ?=0,036 W/(m.K) VS. Multipor, 10 cm, ?=0,040 W/(m.K))
- Secondly to highlight the advantages of a hygroscopic material such as Multipor in case of indoor insulation (see http://www.ytong-silka.de/de/docs/Ytong ... 2_2010.pdf). The frequent problem with indoor insulation is the condensation at the boundary between the insulation and the wall, due to the brutal decrease of the temperature and the difference of the diffusion coefficient.
Here is a schema of the current structure :

Here is a schema of the structure with indoor insulation:

1) I would like to understand the influence of the insulation thickness on the amount of water. I have been testing three thickness (5 cm, 10 cm, 15 cm). But the results are confusing me because they show that the more the insulation is thick, the least is the amount of water :

Normally it should be the opposite.
2) Then I would like to highlight the condensation process at the boundary between the wall and the insulation to prove the interest of the hygroscopic material over the rockwool + vapor barrier.
That is why I have run a simulation with 10 cm of rockwool + 0,1 cm of vapor barrier + a hole representing the non-perfect junction at the boundary.
We observe indeed the increase of the global amount of water. It is not acceptable for the durability of the structure.

But even if I focus on the boundary layer (1 cm thickness) to measure the amount of water, I have no criteria to validate or reject the studied thickness :

Does anyone have any answers to these questions ?
Thank you.
I am a beginner with WUFI 3D and I am wondering a few questions concerning the analysis of the results.
The pursposes of my study are :
- First to compare to types of indoor insulation (rockwool + vapor barrier, 10 cm, ?=0,036 W/(m.K) VS. Multipor, 10 cm, ?=0,040 W/(m.K))
- Secondly to highlight the advantages of a hygroscopic material such as Multipor in case of indoor insulation (see http://www.ytong-silka.de/de/docs/Ytong ... 2_2010.pdf). The frequent problem with indoor insulation is the condensation at the boundary between the insulation and the wall, due to the brutal decrease of the temperature and the difference of the diffusion coefficient.
Here is a schema of the current structure :

Here is a schema of the structure with indoor insulation:

1) I would like to understand the influence of the insulation thickness on the amount of water. I have been testing three thickness (5 cm, 10 cm, 15 cm). But the results are confusing me because they show that the more the insulation is thick, the least is the amount of water :

Normally it should be the opposite.
2) Then I would like to highlight the condensation process at the boundary between the wall and the insulation to prove the interest of the hygroscopic material over the rockwool + vapor barrier.
That is why I have run a simulation with 10 cm of rockwool + 0,1 cm of vapor barrier + a hole representing the non-perfect junction at the boundary.
We observe indeed the increase of the global amount of water. It is not acceptable for the durability of the structure.

But even if I focus on the boundary layer (1 cm thickness) to measure the amount of water, I have no criteria to validate or reject the studied thickness :

Does anyone have any answers to these questions ?
Thank you.