At a certain time step of the calculation, only one iteration is performed and theta and phi are then constantly at 0. The moisture content in the material makes a jump at this point and remains at saturation humidity.
Its a roof construction with insulation between rafters. With Wufi 1D and the same climate conditions I got reasonable results.
What might that be? What settings can I change to get reasonable results with Wufi 2D?
processing - problems with theta and phi
-
Christian Bludau
- WUFI SupportTeam IBP

- Posts: 1242
- Joined: Tue Jul 04, 2006 10:08 pm -1100
- Location: IBP Holzkirchen, the home of WUFI
- Contact:
Re: processing - problems with theta and phi
Hello,
first try to change Computational Settings -> Enhanced URF for RH from 0.7 to 0.3. That decouples the solution of the temperature and the relative humidity and leads to an easier solution of the equations and a better convergence. You can set that as an default, because the default value is quite old, we found out that the solution is easier with 0.3.
If this doesn´t help, please see here, if you can find something useful:
http://www.wufi-forum.com/WUFIForum/vie ... 1354#p1354
http://www.wufi-forum.com/WUFIForum/vie ... 2190#p2190
Christian
first try to change Computational Settings -> Enhanced URF for RH from 0.7 to 0.3. That decouples the solution of the temperature and the relative humidity and leads to an easier solution of the equations and a better convergence. You can set that as an default, because the default value is quite old, we found out that the solution is easier with 0.3.
If this doesn´t help, please see here, if you can find something useful:
http://www.wufi-forum.com/WUFIForum/vie ... 1354#p1354
http://www.wufi-forum.com/WUFIForum/vie ... 2190#p2190
Christian