Photovoltaic panel on the sloped Roof

Post by samiraaien » Tue Nov 26, 2019 9:52 pm -1100

Hi,

I would like to do hygrothermal analysis of sloped roof, which has photovoltaic panels on the roof.
I have two question:

1- Without considering the PV on roof, the results of codensation risk and total water content of construction will be significantlz changed?
2-If yes , how can I consider this panels on my construction at WUFI pro?

Thanks a lot
Samira

Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1130
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: Photovoltaic panel on the sloped Roof

Post by Christian Bludau » Wed Nov 27, 2019 9:39 am -1100

Hi Samira,

the adaption of PV elements on a roof can have a significant influence on the hygrothermal behavior, depending on the kind of elements and the way of shading. If there will be a high airflow possible below the panels, that will have a negative influence.
As far as I know, there are no models for that at the moment. For the shading of flat roofs we there is a WTA-recommendation (6-8), which gives a list of factors for shading. Unfortunately it is not available in English. The PV model is coming from my paper discussed here:
viewtopic.php?p=2790#p2790
Please note (only the first entry is in French, the others are in English.

Christian