Re: KLI FILE

Post by Christian Bludau » Tue Nov 15, 2016 11:00 pm -1100

Hello James,
1 KLI file inputs - is the time sequence 0.00, 0.05.....0.55, 0.60 etc or 0.55, 1.00, 1.05 etc?
Nope, you have to relate it to the hour:
1s = 1/3600; 5s = 5*1/3600 = 0.001388889h
2 Under "Calc Period / Profiles", for "Time step [1h]" - is 0.05 correct for the 5 second step in the recorded data?
No, 0.001388889h
3 Under "Start & End Profiles" - do I adjust the number of hours to match the number of 5 second steps?
In the Start&End-Profiles you can enter the time in hh:mm:ss, so why not enter 00:00:00 to 00:20:00?

Greetings,
Christian

james bertram
WUFI User
WUFI User
Posts: 37
Joined: Sun Aug 11, 2013 9:14 pm -1100

Re: KLI FILE

Post by james bertram » Wed Nov 16, 2016 3:26 pm -1100

Ahh! Thank you learned person :D

...but one more question please. The "Temp Transport Calc" simulation appears to run ok, but when I add "Moisture Transport Calc" the temp outcomes appear not to respond?

Is this because the temp range (up to 1000) is outside the accepted range for moisture calcs?

Happy horse riding, James

Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1130
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: KLI FILE

Post by Christian Bludau » Sun Nov 20, 2016 11:29 pm -1100

Hej James,
your temp range is up to 1000°C?
That exceeds the limits of the calculation model. With that high temperatures the vapor pressure in the assembly is much higher than the atmospheric pressure. The equations of WUFI are not adapted for such conditions.
Best regards,
Christian

james bertram
WUFI User
WUFI User
Posts: 37
Joined: Sun Aug 11, 2013 9:14 pm -1100

Re: KLI FILE

Post by james bertram » Mon Nov 21, 2016 2:02 pm -1100

Thanks Christian - been trying to understand what happens to a wall assembly under ISO 9705 testing...called the full room test because you line a 3.6 x 2.4 x2.4m room and turn on the burner. Temp vary a fair bit, but at the hot end they can reach 1000C.

Been are really useful learning experience, even if the outcomes input are too extreme...wufi= :o :shock: :D

Enjoy the horse riding
James

Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 351
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Re: KLI FILE

Post by Manfred Kehrer » Mon Nov 21, 2016 2:10 pm -1100

James,
I really think that it is important for you to realize that applied thermodynamics in building science, which covers about -30°C to about 70°C, is totally different compared to 1000°.
Manfred