Numerics problem related to roof with airlayer

Post by WEI LI »

Hi, I am trying to simulate the metal roof system with the air layer.
However, the numerics problem always exists.
I have attached the assembly: metal deck - air layer - polyisocyanurate board - metal deck
assembly.jpg
assembly.jpg (70.37 KiB) Viewed 3082 times
Most of the settings are kept as default, such as surface transfer coefficient, initial conditions.
sur.jpg
sur.jpg (69.22 KiB) Viewed 3082 times
The weather of Auckland, NZ from the database is applied as the indoor and outdoor climate.
After the calculation, a lot of convergence failures showed up, and balance 1 and balance 2 are in incredible difference.
numerics.png
numerics.png (22.83 KiB) Viewed 3082 times
I have tried using the adaptive time step, doesn't work.
I have tried using air layer without moisture capacity, doesn't work.
I have tried using surface sd-Value instead of actually insert the metal deck, doesn't work as well.
It is driving me crazy, please help!
Thank you so much
Christian Bludau
WUFI SupportTeam IBP
WUFI SupportTeam IBP
Posts: 1130
Joined: Tue Jul 04, 2006 10:08 pm -1100
Location: IBP Holzkirchen, the home of WUFI
Contact:

Re: Numerics problem related to roof with airlayer

Post by Christian Bludau »

Dear Wei Li,

that may happen due to dew water in the air layer. Try to split it as described here:
viewtopic.php?f=32&t=1777&p=5226#p5226

Further the convergence will be much better, if you do not model the metal sheets as a layer but as a sd-value in the boundary condition.

Christian