Post by Michael Hurd » Thu Dec 07, 2017 9:11 am -1100

A product manufacturer could not provide to me the perm rating of their insulation product. What they could provide me was the Perm rating of their product attached to 1" of concrete that is combined with .375" of granite. I have no idea why they tested their product this way. The concrete/granite assembly has a perm rating of .19, when the 2.5" of insulation is added to the concrete/granite the resulting perm rating, for the three products combined, is .10 perms. From what has been provided to me, Is there a calculation that can be performed to ascertain the perm rating of the 2.5" of insulation only?
Respectfully,

Michael Hurd

Manfred Kehrer
WUFI International Support Team
WUFI International Support Team
Posts: 351
Joined: Thu Mar 10, 2005 2:17 am -1100
Location: Northbrook, IL; USA
Contact:

Re: Cumulative effects of perm ratings in a wall assembly

Post by Manfred Kehrer » Thu Dec 07, 2017 9:41 am -1100

Of course there is.
The resistances add up to the total resistance. Perm is the reciprocal of the resistance. So in this case:
Resistance of insulation = 1/0.1 - 1/0.19 which results in 0.21 perm for your insulation.

(P.S. Next time I will send you an invoice for that :wink: )
Manfred
Wiss, Janney, Elstner Associates, Inc.
Official WUFI® Collaboration Partner for USA/Canada
Enjoy WUFI® :) .... It is easy and complex.

Michael Hurd
WUFI User
WUFI User
Posts: 103
Joined: Thu Oct 19, 2006 5:27 am -1100

Re: Cumulative effects of perm ratings in a wall assembly

Post by Michael Hurd » Thu Dec 07, 2017 10:00 am -1100

Well you can send an invoice, but whether or not I pay it is another matter! As always, thanks!