The U-value is a steady-state parameter. Therefore, to determine it from WUFI 2D, you should define constant indoor and outdoor boundary conditions and run the calculation until the temperature field and heat flows have reached a steady state.
Once steady-state conditions are reached, the U-value ...
Search found 1312 matches
- Fri Nov 13, 2026 2:37 am -1100
- Forum: WUFI 2D
- Topic: U-value calculation for walls using WUFI 2D
- Replies: 2
- Views: 5741
- Wed Nov 11, 2026 11:02 pm -1100
- Forum: WUFI 2D
- Topic: WUFI 2D: wall in a ground depression – boundary conditions for surface water
- Replies: 1
- Views: 2771
Re: WUFI 2D: wall in a ground depression – boundary conditions for surface water
Dear Hüsna,
in principle, parts of this situation can be investigated with WUFI 2D, but there are some important limitations.
The wall, foundation and slab can be represented together in a 2D section, including the surrounding soil. However, WUFI 2D does not simulate groundwater flow or surface ...
in principle, parts of this situation can be investigated with WUFI 2D, but there are some important limitations.
The wall, foundation and slab can be represented together in a 2D section, including the surrounding soil. However, WUFI 2D does not simulate groundwater flow or surface ...
- Wed Nov 11, 2026 10:57 pm -1100
- Forum: WUFI Pro
- Topic: Deckendämmung als verlorene Schalung – Korrosion?
- Replies: 2
- Views: 25404
Re: Deckendämmung als verlorene Schalung – Korrosion?
Hallo,
die in WUFI-Corr hinterlegten Korrosionsansätze bzw. Grenzwerte beziehen sich auf normalen Baustahl. Bei verzinkten Befestigungselementen ist die Korrosionsbeständigkeit daher grundsätzlich anders zu bewerten. Die Ampelfarbe lässt sich nicht unmittelbar auf verzinkte Schrauben übertragen.
Im ...
die in WUFI-Corr hinterlegten Korrosionsansätze bzw. Grenzwerte beziehen sich auf normalen Baustahl. Bei verzinkten Befestigungselementen ist die Korrosionsbeständigkeit daher grundsätzlich anders zu bewerten. Die Ampelfarbe lässt sich nicht unmittelbar auf verzinkte Schrauben übertragen.
Im ...
- Wed Nov 11, 2026 10:51 pm -1100
- Forum: WUFI 2D
- Topic: Shading from PV panels - WUFI 2D
- Replies: 1
- Views: 14116
Re: Shading from PV panels - WUFI 2D
Hi Katrine,
You can model this in WUFI 2D following the same approach described in the guidelines for WUFI Pro regarding shading from PV panels.
https://wufi.de/en/service/downloads/#flatroofs
https://wufi.de/en/service/downloads/#pitched_roofs
Christian
You can model this in WUFI 2D following the same approach described in the guidelines for WUFI Pro regarding shading from PV panels.
https://wufi.de/en/service/downloads/#flatroofs
https://wufi.de/en/service/downloads/#pitched_roofs
Christian
- Wed Nov 11, 2026 10:49 pm -1100
- Forum: Climate
- Topic: Wufi 2D 4.6 misuses weather data by jumping to January in the middle of summer
- Replies: 2
- Views: 33504
Re: Wufi 2D 4.6 misuses weather data by jumping to January in the middle of summer
Hi Joe,
this could possibly be related to the indoor climate settings. What indoor climate model or conditions have you defined for the simulation?
In addition, please check under Computational Parameters → Enhanced whether the time step is set to 3600 s.
Best regards,
Christian
this could possibly be related to the indoor climate settings. What indoor climate model or conditions have you defined for the simulation?
In addition, please check under Computational Parameters → Enhanced whether the time step is set to 3600 s.
Best regards,
Christian
- Wed Nov 11, 2026 10:44 pm -1100
- Forum: Installation
- Topic: Installation of VTT
- Replies: 14
- Views: 123482
Re: Installation of VTT
There are new versions available for the post process modules
Wufi Bio 5.0.2
WUFI Corr 2.0.1
WUFI FinMould 3.0.1
WUFI Decay 1.2.0
with updated runtimes.
If you get an error please first check, if you are using the latest version.
You can find them here:
https://wufi.de/en/software/wufi-add ...
Wufi Bio 5.0.2
WUFI Corr 2.0.1
WUFI FinMould 3.0.1
WUFI Decay 1.2.0
with updated runtimes.
If you get an error please first check, if you are using the latest version.
You can find them here:
https://wufi.de/en/software/wufi-add ...
- Sun Oct 18, 2026 7:30 pm -1100
- Forum: WUFI Pro
- Topic: Large increase in Water content
- Replies: 11
- Views: 46628
Re: Large increase in Water content
Hi Alberto,
The moisture shown in your results is located within the PIR, which is enclosed by vapour-tight aluminium facings on both sides. In a one-dimensional calculation, practically no additional moisture can enter this layer. The variations therefore mainly represent a redistribution of the ...
The moisture shown in your results is located within the PIR, which is enclosed by vapour-tight aluminium facings on both sides. In a one-dimensional calculation, practically no additional moisture can enter this layer. The variations therefore mainly represent a redistribution of the ...
- Fri Oct 02, 2026 1:43 am -1100
- Forum: WUFI Ireland & UK
- Topic: Why does concrete take up moisture?
- Replies: 1
- Views: 44289
Re: Why does concrete take up moisture?
Hi Norbert,
The moisture content of a construction assembly will generally not remain at its initial value indefinitely. Instead, the materials gradually adjust towards a long-term equilibrium condition that is influenced by both the interior and exterior climate.
In your model, the concrete was ...
The moisture content of a construction assembly will generally not remain at its initial value indefinitely. Instead, the materials gradually adjust towards a long-term equilibrium condition that is influenced by both the interior and exterior climate.
In your model, the concrete was ...
- Tue Sep 29, 2026 11:18 pm -1100
- Forum: WUFI Pro
- Topic: Aluminium Panel
- Replies: 8
- Views: 8167
Re: Aluminium Panel
1- If I follow the guideline on “Assessing the Risk of Interstitial Condensation Runoff,” what minimum RC value should I consider? I ask because I do not have a water- and vapour-tight surface in my assembly, and I do not consider it would be appropriate to consider the concrete layer as one ...
- Tue Sep 29, 2026 11:05 pm -1100
- Forum: WUFI Pro
- Topic: Aluminium Panel
- Replies: 8
- Views: 8167
Re: Aluminium Panel
The runoff guideline can be applied to condensation forming on the foil surface facing the cavity. However, it does not assess moisture accumulation inside the closed-cell PIR itself. For a smooth, water- and vapour-tight foil surface without adjacent fibrous insulation, the guideline starts with a ...
- Tue Sep 29, 2026 10:56 pm -1100
- Forum: WUFI Pro
- Topic: Large increase in Water content
- Replies: 11
- Views: 46628
Re: Large increase in Water content
In WUFI, liquid water cannot accumulate directly between two adjacent material layers because the model does not represent an interface cavity. If you want to evaluate interstitial condensation and possible runoff at an interface, you would need to introduce an explicit air layer in the model ...
- Wed Sep 16, 2026 2:58 am -1100
- Forum: WUFI Pro
- Topic: Large increase in Water content
- Replies: 11
- Views: 46628
Re: Large increase in Water content
Hi Alberto,
regarding your questions:
1) yes, the condensation in air layers part
2) yes, the Rmet values - these should always be used if there is at least one metallic surface connected to the air gap
Christian
regarding your questions:
1) yes, the condensation in air layers part
2) yes, the Rmet values - these should always be used if there is at least one metallic surface connected to the air gap
Christian
- Fri Aug 21, 2026 12:49 am -1100
- Forum: WUFI Pro
- Topic: Aluminium Panel
- Replies: 8
- Views: 8167
Re: Aluminium Panel
Hi Alberto,
Aluminum bright, dry vs. wet
The different long-wave emissivities are based on measurements from a research project and reflect the fact that bright aluminum behaves very differently when its surface is dry or covered by a thin water film. In practice, façade surfaces are often ...
Aluminum bright, dry vs. wet
The different long-wave emissivities are based on measurements from a research project and reflect the fact that bright aluminum behaves very differently when its surface is dry or covered by a thin water film. In practice, façade surfaces are often ...
- Tue Aug 11, 2026 11:00 pm -1100
- Forum: WUFI Pro
- Topic: Aluminium Panel
- Replies: 8
- Views: 8167
Re: Aluminium Panel
Hi Alberto,
I would recommend leaving the aluminium panel itself out of the assembly and instead accounting for its vapour diffusion resistance through an additional diffusion resistance (sd-value) in the surface transfer conditions.
For the exterior surface properties, use the short-wave ...
I would recommend leaving the aluminium panel itself out of the assembly and instead accounting for its vapour diffusion resistance through an additional diffusion resistance (sd-value) in the surface transfer conditions.
For the exterior surface properties, use the short-wave ...
- Mon Aug 03, 2026 7:02 pm -1100
- Forum: General
- Topic: Differences in water content results between WUFI Pro and WUFI 2D with identical setups
- Replies: 7
- Views: 85601
Re: Differences in water content results between WUFI Pro and WUFI 2D with identical setups
Well done, thanks for sharing this pictures.
Have fun
Christian
Have fun
Christian